The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

SWA Cable Above ground and earthing the armour

When using SWA cable underground I always earth the armour, regardless of whether the armour is used as the cpc or not. The armour does provide some mechanical protection and it is important that the armour is earthed so that if the cable were penetrated (e.g. by a garden fork), the supply would automatically be disconnected by the protective device under this fault condition.
I have a situation on an existing domestic installation where I will be changing the consumer unit.  The 3-core SWA cable to the hot-tub rotary isolator is above ground and clipped to an outside wall.
The cable has not been terminated with brass glands, and at the ends the armour have been taped up, so no exposed conductive parts. The armour is not being used as the cpc.
At the rotary isolator for the hot-tub, stuffing glands have been used. The cable feeding the hot-tub does rest on the ground for about 1m before going into the hot-tub enclosure.
The earthing arrangement is TNCS, however at the hot-tub rotary isolator, the TNCS earth is not exported and there is an earth electrode for  the hot-tub’s cpc
Would you expect the armour to be earthed? Is it acceptable to terminate SWA without brass glands?
Parents

  • sparkiemike:




    Chris Pearson:



    Zoomy, who said that the cable is on the ground?


    What's the alternative - a bit of T&E. There's a bit of T&E at daughter's house which is dry and crazed. She got a bit upset when I started digging with my thumbnail. ? The plan is to replace it with some T&E, but perhaps I am being misguided - is SWA better, or worse, or the same, when it comes to exposure to sunlight (on a south-facing wall)?


     




    I did 



    The cable feeding the hot-tub does rest on the ground for about 1m before going into the hot-tub enclosure.



     




    I must polish my reading glasses. ?

Reply

  • sparkiemike:




    Chris Pearson:



    Zoomy, who said that the cable is on the ground?


    What's the alternative - a bit of T&E. There's a bit of T&E at daughter's house which is dry and crazed. She got a bit upset when I started digging with my thumbnail. ? The plan is to replace it with some T&E, but perhaps I am being misguided - is SWA better, or worse, or the same, when it comes to exposure to sunlight (on a south-facing wall)?


     




    I did 



    The cable feeding the hot-tub does rest on the ground for about 1m before going into the hot-tub enclosure.



     




    I must polish my reading glasses. ?

Children
No Data