Just wondering what peoples thoughts are to mixing makes of MCB's and RCD's in consumer units. I went to a callout the other night and the culprit was a faulty 61008 RCD. To get the power back on I replaced the faulty Item with a different make of 61008 RCD. The next day I raised a job to have the right make of RCD fitted. It turns out the QS at work isn't concerned about the incorrect make of RCD and is more concerned about IP ratings being met. Am I right in wanting to fit the correct make of RCD?


What would you code this as on a EICR?
Parents
  • For several years I have been flagging pick and mix protective devices in consumer units when I have been preparing EICRs at change of tenancy for a housing association, before the 18th Edition was published. I’m told that currently they are getting a national contractor to go through the whole site to do periodic EICRs for every flat, since the introduction of the 18th I have coded the issue as a three, I would like to know what the national contractors guys are saying about them.


    Andy
Reply
  • For several years I have been flagging pick and mix protective devices in consumer units when I have been preparing EICRs at change of tenancy for a housing association, before the 18th Edition was published. I’m told that currently they are getting a national contractor to go through the whole site to do periodic EICRs for every flat, since the introduction of the 18th I have coded the issue as a three, I would like to know what the national contractors guys are saying about them.