MCB and RCD mix and match of makes 536.4.203

Just wondering what peoples thoughts are to mixing makes of MCB's and RCD's in consumer units. I went to a callout the other night and the culprit was a faulty 61008 RCD. To get the power back on I replaced the faulty Item with a different make of 61008 RCD. The next day I raised a job to have the right make of RCD fitted. It turns out the QS at work isn't concerned about the incorrect make of RCD and is more concerned about IP ratings being met. Am I right in wanting to fit the correct make of RCD?


What would you code this as on a EICR?
Parents
  • I phoned two manufacturers to ask if I could put a RCBO made by one into the other one's consumer unit as it needed a B32/30mA type A RCBO due to tripping issues and the original consumer unit manufacturer does not make type A RCBO or RCDs.


    What response do you think I received?


    Andy
Reply
  • I phoned two manufacturers to ask if I could put a RCBO made by one into the other one's consumer unit as it needed a B32/30mA type A RCBO due to tripping issues and the original consumer unit manufacturer does not make type A RCBO or RCDs.


    What response do you think I received?


    Andy