Type-A RCD failing 180 degree ramp test

Former Community Member
Former Community Member
Hi


We are testing a type-A RCD (see image: "ABB") with a METREL MI 3152 (see image: "MI 3152 test").

As the image shows, the ramp test (I delta) is failing to trip the RCD for the negative half wave.


Have oneone seen this before?


Br Sebastian
attachments.zip
Parents
  • Former Community Member
    0 Former Community Member

    sparkiemike:




    Sparkingchip:

    Is it actually doing a ramp test?




    Don't think so, I think is the RCD tripping time because in the image the results on the instrument are in milliseconds


     




    It is failing the test that is shown as ">1500 mA" on the display. This is a "trip-out current test" (see: Metrel 3152 manual, page 108) The "trip-out test" is described as: "The instrument increases the test current in small steps through appropriate range as follows" see page: 107.


    The test stops at 1500 mA, and the test fails

Reply
  • Former Community Member
    0 Former Community Member

    sparkiemike:




    Sparkingchip:

    Is it actually doing a ramp test?




    Don't think so, I think is the RCD tripping time because in the image the results on the instrument are in milliseconds


     




    It is failing the test that is shown as ">1500 mA" on the display. This is a "trip-out current test" (see: Metrel 3152 manual, page 108) The "trip-out test" is described as: "The instrument increases the test current in small steps through appropriate range as follows" see page: 107.


    The test stops at 1500 mA, and the test fails