This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Type-A RCD failing 180 degree ramp test

Former Community Member
Former Community Member
Hi


We are testing a type-A RCD (see image: "ABB") with a METREL MI 3152 (see image: "MI 3152 test").

As the image shows, the ramp test (I delta) is failing to trip the RCD for the negative half wave.


Have oneone seen this before?


Br Sebastian
attachments.zip
Parents
  • yes that is a "ramp test" to the older hands among us.


    If you can please re-test, lying to the meter that it is an AC type, and also verify that all phase to phase voltages are similar.

    how is the meter connected - how are you choosing the phases to test - your diagram may imply live no1 and earth ,

    does it work if you shuffle them  and use say L3 and earth ?


    Is this the only RCD of its type you have tested with this meter, or has another one tested OK?


    What is the NE voltage, and where is the NE bond ?


Reply
  • yes that is a "ramp test" to the older hands among us.


    If you can please re-test, lying to the meter that it is an AC type, and also verify that all phase to phase voltages are similar.

    how is the meter connected - how are you choosing the phases to test - your diagram may imply live no1 and earth ,

    does it work if you shuffle them  and use say L3 and earth ?


    Is this the only RCD of its type you have tested with this meter, or has another one tested OK?


    What is the NE voltage, and where is the NE bond ?


Children
No Data