mapj1:
yes that is a "ramp test" to the older hands among us.
If you can please re-test, lying to the meter that it is an AC type, and also verify that all phase to phase voltages are similar.
how is the meter connected - how are you choosing the phases to test - your diagram may imply live no1 and earth ,
does it work if you shuffle them and use say L3 and earth ?
Is this the only RCD of its type you have tested with this meter, or has another one tested OK?
What is the NE voltage, and where is the NE bond ?
mapj1:
yes that is a "ramp test" to the older hands among us.
If you can please re-test, lying to the meter that it is an AC type, and also verify that all phase to phase voltages are similar.
how is the meter connected - how are you choosing the phases to test - your diagram may imply live no1 and earth ,
does it work if you shuffle them and use say L3 and earth ?
Is this the only RCD of its type you have tested with this meter, or has another one tested OK?
What is the NE voltage, and where is the NE bond ?