The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
seko:
sparkiemike:
Sparkingchip:
Is it actually doing a ramp test?Don't think so, I think is the RCD tripping time because in the image the results on the instrument are in milliseconds
It is failing the test that is shown as ">1500 mA" on the display. This is a "trip-out current test" (see: Metrel 3152 manual, page 108) The "trip-out test" is described as: "The instrument increases the test current in small steps through appropriate range as follows" see page: 107.
The test stops at 1500 mA, and the test fails
seko:
sparkiemike:
Sparkingchip:
Is it actually doing a ramp test?Don't think so, I think is the RCD tripping time because in the image the results on the instrument are in milliseconds
It is failing the test that is shown as ">1500 mA" on the display. This is a "trip-out current test" (see: Metrel 3152 manual, page 108) The "trip-out test" is described as: "The instrument increases the test current in small steps through appropriate range as follows" see page: 107.
The test stops at 1500 mA, and the test fails
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site