Type-A RCD failing 180 degree ramp test

Former Community Member
Former Community Member
Hi


We are testing a type-A RCD (see image: "ABB") with a METREL MI 3152 (see image: "MI 3152 test").

As the image shows, the ramp test (I delta) is failing to trip the RCD for the negative half wave.


Have oneone seen this before?


Br Sebastian
attachments.zip
Parents
  • Former Community Member
    0 Former Community Member
    Hi


    Here are some updates:


    The RCD has been tested outside the installation (see: "test setup") A current sense resistor of 1 ohm is inserted in series with the green earth cable (not visible on the image).


    The scope recording can be seen in "Full recording". The failing ramp test (negative) is marked with "6" and zoomed versions are "6-1" and 6-1-1"

    METREL has verified that the tester makes a pre-test as seen in "6"


    To me the waveform shape looks good (despite some small spikes) and the RMS values are also reaching 1.5 A before the test stops and fails because the RCD didn't trip. So it must be a faulty RCD or are these minor spikes the reason?

    attachments.zip
Reply
  • Former Community Member
    0 Former Community Member
    Hi


    Here are some updates:


    The RCD has been tested outside the installation (see: "test setup") A current sense resistor of 1 ohm is inserted in series with the green earth cable (not visible on the image).


    The scope recording can be seen in "Full recording". The failing ramp test (negative) is marked with "6" and zoomed versions are "6-1" and 6-1-1"

    METREL has verified that the tester makes a pre-test as seen in "6"


    To me the waveform shape looks good (despite some small spikes) and the RMS values are also reaching 1.5 A before the test stops and fails because the RCD didn't trip. So it must be a faulty RCD or are these minor spikes the reason?