This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Parallel cable sizing

Hi, I'm currently completing my project report for BEng based on an existing install at work. The install is between a 1000 kVA trans to main section board, the existing cable is 5x 240mm 4C SWA in duct buried. All ACB on the circuit are 1600A, I calc the max output of the trans at 1443A. 

I'm trying to prove the existing install using the BS 18th regs as the installer hasn't supplied any, and this is where I'm having an issue. 

From my understanding rating factors must be applied to In (protective device) and that value must be less than or equal to It (tabulated current carrying capacity of a cable). I've got a 'new' In value of 2962A which Ive divided by 5 (number of cores per phase) which gives 592A. Am I right in thinking that I then need to specify a cable using the 592A value? If that is correct than the existing install is incorrect? 

In table 4E4A (18th regs) the max current for 240 SWA multi core, ref D (buried) is 324A. 

Have I gone wrong at some point? 


Any help is very much appreciated, thanks Adam.
Parents
  • Former Community Member
    0 Former Community Member
    Hi ARW182,


    Would you be able to expand on this a bit more? How did you get to the max output of 1443A and then the new In value of 2962? I'm struggling to see how you've got from a 1000kVA Tx to those values, maybe because I've been out of the classroom for too long, but it'd be nice to have a refresher!


    Regards,


    S
Reply
  • Former Community Member
    0 Former Community Member
    Hi ARW182,


    Would you be able to expand on this a bit more? How did you get to the max output of 1443A and then the new In value of 2962? I'm struggling to see how you've got from a 1000kVA Tx to those values, maybe because I've been out of the classroom for too long, but it'd be nice to have a refresher!


    Regards,


    S
Children
No Data