Parallel cable sizing

Hi, I'm currently completing my project report for BEng based on an existing install at work. The install is between a 1000 kVA trans to main section board, the existing cable is 5x 240mm 4C SWA in duct buried. All ACB on the circuit are 1600A, I calc the max output of the trans at 1443A. 

I'm trying to prove the existing install using the BS 18th regs as the installer hasn't supplied any, and this is where I'm having an issue. 

From my understanding rating factors must be applied to In (protective device) and that value must be less than or equal to It (tabulated current carrying capacity of a cable). I've got a 'new' In value of 2962A which Ive divided by 5 (number of cores per phase) which gives 592A. Am I right in thinking that I then need to specify a cable using the 592A value? If that is correct than the existing install is incorrect? 

In table 4E4A (18th regs) the max current for 240 SWA multi core, ref D (buried) is 324A. 

Have I gone wrong at some point? 


Any help is very much appreciated, thanks Adam.
Parents
  • Former Community Member
    0 Former Community Member
    The op appears to be using a correction factor of 0.54??


    It》In/correction factor


    1600/0.54 = 2692 Amps


    It/n = 2692/5 = 592 Amps


    We need to understand how the correction factors have been selected. 

    The LV tails protective device Ir setting could be adjusted to match the transformers LV output.


    Looking a data sheet for a Wilson 11000/415V 1000kVA Tx, full load current at normal tap is stated as HV side 52.5A LV side 1391A.


    Regards

    Parsley
Reply
  • Former Community Member
    0 Former Community Member
    The op appears to be using a correction factor of 0.54??


    It》In/correction factor


    1600/0.54 = 2692 Amps


    It/n = 2692/5 = 592 Amps


    We need to understand how the correction factors have been selected. 

    The LV tails protective device Ir setting could be adjusted to match the transformers LV output.


    Looking a data sheet for a Wilson 11000/415V 1000kVA Tx, full load current at normal tap is stated as HV side 52.5A LV side 1391A.


    Regards

    Parsley