LV 400V AC armoured cable glands are geeting overheat(Temp. measured more than 60 deg C)

Hello Electrical Team.

I would like to discuss an issue being facing in our Power plant(90MW). Our plant generation voltage is 11KV & Plant auxiliary & MCC voltage is 400V AC 50Hz. We have two sections of Power plant PP1 & PP2. In PP2 we are facing issue in LV MCC Panels. 

In LV system we have two BUS A & B. Both BUS's are getting power from their individual T/F(11KV/400V AC) & from here power is distributed to various MCC panels in plant. 

Booster no. 1 MCC have two LV breakers(Q1 & Q2) which are getting power from BUS A & B.

During last week we were found that Q1 breaker incoming cable insulation was melted around the cable gland area & checked the other glands also & they are also found overheated with abnormal temperature. then we took changeover to Q2 breaker but this is also now getting overheat. In main LV distribution panel side also cable glands are getting overheat which are connected to Q1 & Q2 breakers in MCC.

In one phase two cable are laid & connected, size is 400 sq.mm Armoured cable. R phase(L1 & L2), Y Phase(L1 &L2) & B Phase(L1 & L2). The current also not equal in two length of each phase.Pl see the below readings.
Line

Without Armoured

With Armoured

R Phase

L11

195 A

328A

115A

174A

L12

137 A

72A

Y Phase

L21

103A

332A

145A

306A

L22

167A

175A

B Phase

L31

150A

328A

120A

317A

L32

183A

199A


without armoured = Cable outside of MCC before entry in panel.

with armoured = After gland inside the panel. 

Team kindly go through the above said issue & your kind comments will be highly appreciated.
Parents
  • Hello Team,

    The gland plate material is aluminum but gland itself not a brass material, this is sure, gland looks like steel. 

    LV Cables only get hot in length of 3--4 inches from glands after that the cable temperatures are normal. Complete gland plate area also hot. 

    That White color is cooling fan which was recently installed near overheated glands area to keep temperature in normal range. This was not a part of original design. 

    Both the glands plates are very near to each other. 

Reply
  • Hello Team,

    The gland plate material is aluminum but gland itself not a brass material, this is sure, gland looks like steel. 

    LV Cables only get hot in length of 3--4 inches from glands after that the cable temperatures are normal. Complete gland plate area also hot. 

    That White color is cooling fan which was recently installed near overheated glands area to keep temperature in normal range. This was not a part of original design. 

    Both the glands plates are very near to each other. 