Shepherds hut
Former Community Member
I’ve been asked to do an Eicr on a shepherds hut and the supply to it, only had a quick look. The supply is from a farmhouse tncs earthing arrangement to a commando socket. The hut is all wood except chassis which is steel. I think it would probably fall within the definition of caravan for bs7671 so with the tncs would not meet the regs. However since the thing is entirely wood except for the chassis is there an argument for a c3 code?
Highly unlikely it's a TN-C system - more likely TN-C-S - which isn't the same and so not prohibited. (BS 7671 does allow TN-C systems generally (under prescribed circumstances) - see section 543.4).