Recommended checks before CU change

Former Community Member
Former Community Member
As most of you know I’ve only been qualified for just over a year and I’ve got a quote to do for a cu upgrade.


I know I’m nowhere experienced enough to do EICR’s yet, but what would you guys recommend I check/test before doing the cu upgrade and should I do these checks/tests at the quote stage?
Parents
  • Former Community Member
    0 Former Community Member
    I would check the tails and earthing conductor, zs on a couple of existing circuits etc. 

    i would also include a disclaimer should the cu change bring other faults to light. 


Reply
  • Former Community Member
    0 Former Community Member
    I would check the tails and earthing conductor, zs on a couple of existing circuits etc. 

    i would also include a disclaimer should the cu change bring other faults to light. 