davezawadi:
Reading this makes me realise just how badly thought out EV charging is (again). Typically every multiple EV charging point is defective because each has its own electrode following the regs. Two adjacent cars can be at differing potentials. Chris is quite correct here (and BS7671 a mess) because a TT installation inherently depends on the RCD to provide shock protection, and therefore ANY fault with danger must simply trip the RCD if contacted. Simple enough and has worked very well for many years. However people are now worrying about potentials rather than disconnection on contact, which is simply not sensible.
TT does not work unless there is a potential and earth path sufficient to trip the RCD! My reading of multiple earth systems is a TN-S and a TT one, not two TT systems, because they are inherently protected from danger by the RCDs. TT islands do not work for car charging unless you trust the RCD.
Clearly some do not, and the "what if" question immediately makes all this unworkable, particularly when the H&S police have had a go too! The answer is simple and can be fixed immediately by a simple bit of legislation; "Electric vehicles must be class 2, otherwise they may not be sold in the UK". All those not complying may be sent abroad when sold, and the owners suffer a loss like my diesel car, government about turns included! Fair enough and the proper way to sort the problem, which should never have happened in the first place if those responsible had been paying suitable attention!
Exposed-conductive-parts of a TT system are at the potential of the TT system main earth terminal (which is hopefully the potential of the earth electrode).
I'd respectfully suggest that
Exposed-conductive-parts of a TT system should be at the or near the potential of the terra firma earth, that is to say the stuff you may stand on, whcih is a potential aquired by connection to the electrode. If the ground voltage is bouncing up and down because of a fault on a PME network nearby, ideally you would want all CPCs and earthed metal work to bounce up and down with it, in the same way that a fence post will.
I see nothing special about the electrode of a TT system, it's purpose in this context is to make sure that metal objects are at the same potential as the (terra firma) ground they stand on.
Its other purpose is to fire an RCD if there is a live to CPC fault.
mapj1:
I am not aware of any equivalent distance rules for caravans and boats, that prevent say a cold water supply pipe in a marina, from being bonded to the PME supply in the building where it originates, but that is also PME earthed metal. If you had a distribution pillar and meters in a boat yard, if it is the end of the PME service, there will be an electrode on it, even if all the loads are wired as TT.
In terms of is it a real problem, actually the current regs require all properties to bond cold water pipes if they are metal, and no insulation section, and I am aware of a few round here, where one house is PME and the one next door is TT. Many such earthing systems are already linked, like it or not - that is why we do see quite large diverted currents on the pipework sometimes, but it all works OK.
As I said above, the rules are written such that in small space you really cannot win.
Which probably means the rules need a rethink for this case.
My reading of multiple earth systems is a TN-S and a TT one, not two TT systems, because they are inherently protected from danger by the RCDs.
Sparkingchip:
Here in Worcester there are two EV charging stations on the second floor of a multi storey car park that is above the shopping centre service area, what earthing system is currently required for such an installation?
Andy