Bonding 18th edition ?

Hi guys with the new rules with main bonding in the 18th edition how are you all implementing this.


So is it now a complete no go with the mains bonding unless it has a earth potential once its entered the house ? or is it just optional ?
Parents
  • 544.1.2 The main protective bonding connection to any extraneous-conductive-part such as gas, water or

    other metallic pipework or service shall be made as near as practicable to the point of entry of that part into the

    premises.
    Where there is a meter, isolation point or union, the connection shall be made to the consumer’s hard metal

    pipework
    and before any branch pipework. Where practicable the connection shall be made within 600 mm of the

    meter outlet union or at the point of entry to the building if the meter is external.


Reply
  • 544.1.2 The main protective bonding connection to any extraneous-conductive-part such as gas, water or

    other metallic pipework or service shall be made as near as practicable to the point of entry of that part into the

    premises.
    Where there is a meter, isolation point or union, the connection shall be made to the consumer’s hard metal

    pipework
    and before any branch pipework. Where practicable the connection shall be made within 600 mm of the

    meter outlet union or at the point of entry to the building if the meter is external.