This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Connecting Multiple Bemco/Ryefield Boards

Ok I have a new build project where one Bemco/Ryefield board is not large enough to cover all apartments. 


I will need to install 3 to cover the number of outgoing ways required.


My questions is this. Given that there is one incoming bulk supply, what options are there to split it between the three? I know Lucy do an MSDB with a vertical busbar. Would the DNO accept daisy chaining these together? Or should we use a busbar chamber and tap-off to each board?


Any advice would be gratefully received.
Parents
  • Hi Simon


    its SP Energy Networks on this one.
Reply
  • Hi Simon


    its SP Energy Networks on this one.
Children
No Data