Connecting Multiple Bemco/Ryefield Boards

Ok I have a new build project where one Bemco/Ryefield board is not large enough to cover all apartments. 


I will need to install 3 to cover the number of outgoing ways required.


My questions is this. Given that there is one incoming bulk supply, what options are there to split it between the three? I know Lucy do an MSDB with a vertical busbar. Would the DNO accept daisy chaining these together? Or should we use a busbar chamber and tap-off to each board?


Any advice would be gratefully received.
Parents

  • Simon Gallagher:

    I just had a quick look at SPENs earthing policy, and like most of the other DNOs they don’t seem to allow multiple services into ‘multiple occupied buildings’. . . 




    We would, providing the Ryefields were all next to each other. 


    Regards,


    Alan. 

Reply

  • Simon Gallagher:

    I just had a quick look at SPENs earthing policy, and like most of the other DNOs they don’t seem to allow multiple services into ‘multiple occupied buildings’. . . 




    We would, providing the Ryefields were all next to each other. 


    Regards,


    Alan. 