mapj1:
Ah, but not so unusual to have a different DNO approved sub contractor for the first set , with a less rigorous checking of the rules than the one making the most recent visits. I suspect the DNO and the book of rules have not changed any time recently, but rather the interpretation of what sort of installation it should be treated as, and so if it is sensible to connect or not.
After all BS7671 section 462 and thereabout could be read to indicate that there should be a single clear point of isolation at the origin, not multiple ones, but henley blocks and multiple consumer units are very common.
Chris Pearson:
FWIW, 537.1.4 has migrated to 462.1.201, but the words remain the same.
MHRestorations:
Those isolators always confuse me a little. Is this a new demarcation point, beyond the consumer side of the meter? If so, who owns it. If the customer, then BS7671 applies and it should be non combustible.
If a contractor fits one... does it then become the DNO's property de-facto, or is the contractor in breach of the regs for a combustible switchgear enclosure?
This does need working out.
I understand the reason for insulated enclosures (TT systems, pre RCD....) but surely there could be a non combustible but non conductive enclosure (phenolic anyone?) that bridges the gap?