Crazy having 2 small boards, must have got them for free.
WB³:
Chris Pearson:
It's getting away from the OP, but what about the supplier's isolator? (Oh, the grief that that caused me!)Hi Chis, what grief was caused? I really like good chunky Omni pole isolator that has been made available to connect a BS7671 compliant installation to, where the supply side is sealed and the outgoing side not. Does removing the suppliers fuse to isolate the main incoming terminals of a standard Consumer unit comply with BS7671?
Chris Pearson:
It's getting away from the OP, but what about the supplier's isolator? (Oh, the grief that that caused me!)
MHRestorations:
Those isolators always confuse me a little. Is this a new demarcation point, beyond the consumer side of the meter? If so, who owns it. If the customer, then BS7671 applies and it should be non combustible.
If a contractor fits one... does it then become the DNO's property de-facto, or is the contractor in breach of the regs for a combustible switchgear enclosure?
This does need working out.
I understand the reason for insulated enclosures (TT systems, pre RCD....) but surely there could be a non combustible but non conductive enclosure (phenolic anyone?) that bridges the gap?
Chris Pearson:
FWIW, 537.1.4 has migrated to 462.1.201, but the words remain the same.