DNO connection

A contractor has provided the single-phase electrical installation in 12 new, very small, individual commercial units. For whatever reason he provided two 6way distribution boards one appears to be for lighting and the like and the other for power, both with 30mA overall RCD protections both boards have a main switch. The tails for both boards are brought to a set of ISCOs from which he left a short tail connection for the meter. Now 4 of the units have been connected to the supply but apparently connection is being refused to the remaining units as no main switch has been provided. I guess different DNOs, different rules and indeed attitudes but I can find no reference to the need for a main switch in the DNO connection guide other than that the installation has to comply with 7671.

  • Crazy having 2 small boards, must have got them for free.



    In some circumstances there can be a requirement to be able to meter lighting and power loads separately (for local energy management purposes, not supplier billing) - so several separate boards might not be such a silly idea.

       - Andy.

  • WB³:




    Chris Pearson:

    It's getting away from the OP, but what about the supplier's isolator? (Oh, the grief that that caused me!)




    Hi Chis, what grief was caused? I really like good chunky Omni pole isolator that has been made available to connect a BS7671 compliant installation to, where the supply side is sealed and the outgoing side not. Does removing the suppliers fuse to isolate the main incoming terminals of a standard Consumer unit comply with BS7671?



    Having put in my own isolator, I really didn't want another one in series with it. I got my own way in the end, and compensation from the Ombudsman.

  • Former Community Member
    0 Former Community Member

    Chris Pearson:

    It's getting away from the OP, but what about the supplier's isolator? (Oh, the grief that that caused me!)


     




    Hi Chis, what grief was caused? I really like good chunky Omni pole isolator that has been made available to connect a BS7671 compliant installation to, where the supply side is sealed and the outgoing side not. Does removing the suppliers fuse to isolate the main incoming terminals of a standard Consumer unit comply with BS7671?

  • It's getting away from the OP, but what about the supplier's isolator? (Oh, the grief that that caused me!)


    TN installation => REC2 switch in a plastic enclosure.


    TT installation => RCD in the same enclosure. Then you don't need one for the "master switch" in the CU.

  • MHRestorations:

    Those isolators always confuse me a little. Is this a new demarcation point, beyond the consumer side of the meter? If so, who owns it. If the customer, then BS7671 applies and it should be non combustible.


    If a contractor fits one... does it then become the DNO's property de-facto, or is the contractor in breach of the regs for a combustible switchgear enclosure?


    This does need working out.


    I understand the reason for insulated enclosures (TT systems, pre RCD....) but surely there could be a non combustible but non conductive enclosure (phenolic anyone?)  that bridges the gap?




    The NICEIC told me:


    • In a domestic setting, an RCD in its own enclosure is considered 'similar switchgear' re BS EN 61439-3, so it should be a non-combustible enclosure.

    • 'If' an RCD was installed upstream of a non-combustible CU on a TT installation, the enclosure would have to be non-combustible (even though I argued the RCD offers fault protection to the CU, so would just be shifting the problem of no fault protection to the RCD enclosure, so you'd need an RCD upfront of that, and so on).

    •  An RCD upstream of the metal CU on TT is not needed anyway, so no need to worry about using a metal enclosure for the RCD because it wouldn't be there, and there's no need for the RCD because an insulated gland should be used for the 'double insulated' tails so the tails don't contact the metal enclosure at the point of entry, so won't touch the metal anyway (even though I argued that the RCD would offer fault protection for the metal CU 'if' in a split load board the tails or the single insulated linking conductors to the RCCB's inside the board ever became damaged and contacted the metal CU).


    Others may of course disagree.


    F

  • Chris Pearson:

    FWIW, 537.1.4 has migrated to 462.1.201, but the words remain the same.




    It is interesting Chris that 462.1.201 refers to a main linked switch or circuit breaker, both singular terms not plural.  This device to be positioned as near as practicable to the origin of every installation. It must be double pole switching for ordinary folk for a single phase installation and be capable of switching the supply ON LOAD. 


    This "isolator" must be able to disconnect when carrying a full load current. So it is more than an "isolator" as defined  on page 31 which can also be called a "disconnector."  A "disconnector" is defined on page 27  in note 2 as being able only to be capable of opening or closing a circuit when either a negligible current is broken or made, or when no significant change in Voltage across the terminals of each pole of the disconnector occurs."


    So the device is a "SWITCH, LINKED" as defined on page 37, even though it affords "isolation". So it is best not to call it an "isolator."


    Z.

  • FWIW, 537.1.4 has migrated to 462.1.201, but the words remain the same.
  • Former Community Member
    0 Former Community Member
     I can find no reference to the need for a main switch in the DNO connection guide other than that the installation has to comply with 7671


    Has 537.1.4 changed since amd3 :2015 to have the first word as plural?


    Regards


    BOD
  • Personally I wouldn't accept that a stand alone isolator is a similar switchgear assembly to a DBO, and therefore I don't believe that any Regulation is breached by the installation of such.
  • Those isolators always confuse me a little. Is this a new demarcation point, beyond the consumer side of the meter? If so, who owns it. If the customer, then BS7671 applies and it should be non combustible.


    If a contractor fits one... does it then become the DNO's property de-facto, or is the contractor in breach of the regs for a combustible switchgear enclosure?


    This does need working out.


    I understand the reason for insulated enclosures (TT systems, pre RCD....) but surely there could be a non combustible but non conductive enclosure (phenolic anyone?)  that bridges the gap?