Sparkingchip:
Am I right in thinking the clamp test will only work on multiple interconnected electrodes, so for a single earth electrode you need to use long test leads to temporary stakes?
Andy
OMS:
Sparkingchip:
Am I right in thinking the clamp test will only work on multiple interconnected electrodes, so for a single earth electrode you need to use long test leads to temporary stakes?
Andy
The test clamp only isolates the electrode under test - generally where at the end of every down conductor, there is an electrode - and a test clamp to just separate the connection (above ground rather than scrabbling about in the electrode pit).
Once you have the electrode isolated, then typically a fall of potential or wenner test will give you a value if you have a suitable reference electrode (and usually you also need a "moveable" electrode for the so called 4 wire test)
Regards
OMS
Zoomup:
Thanks all. The church has been quoted about £65 for the testing, but only if four churches are tested at one time on one day and are close together, .... The cost seems very low to me.
Z.