Multi-core SWA cable installation in vertical risers.

Hi


I have just had a conversation with a contractor who has stipulated that as part of a vertical cable installation it is a requirement to put a kink in the cable every 5-7m. The reason behind this is they say it helps with the distribution of the weight on high vertical risers.


I have never heard of anyone doing this? can someone please advise me if this is now a requirement, or point me in the right direction for clarification, i.e. is it in any of the guidance notes.


Regards


Desmond Young BSc (Hons) (Open) MSc.
Parents

  • Chris Pearson:

    OK, so the cable is cleated say every 500 mm and kinked every 5 m. If the nine cleats below the kink fail, how will the tenth one support the cable? ?



    If nine cleats failed, then you did it wrong, and the tenth one is probably about to fail anyway. 

     

Reply

  • Chris Pearson:

    OK, so the cable is cleated say every 500 mm and kinked every 5 m. If the nine cleats below the kink fail, how will the tenth one support the cable? ?



    If nine cleats failed, then you did it wrong, and the tenth one is probably about to fail anyway. 

     