VOLTAGE BETWEEN THE GENERAL MASS OF EARTH AND A PME NEUTRAL/EARTH

Other than under fault conditions or a small difference due to volt drop on a heavily loaded CNE cable can anyone explain why you may get a large potential difference (say 70V) between the general mass of earth and the MET on a an installation with a PME earthing system?


I have not seen this myself. If this does occur how rare or frequent might this circumstance occur?


If this potential difference does occur what sort of duration might this persist for?


Although a DNO may switch occasionally the HV ring for fault or maintenance works transformer neutrals remain bolted to earth and if the HV/LV earths are combined then an earth resistance of sub 1 ohm (in UKPN land that is what they want) so how can the neutral voltage float up more than a couple of volts above the general mass of earth?
Parents
  • Former Community Member
    0 Former Community Member
    I refused to have a PME supply when it was offered. My supply was OH TT, the earth electrode was a rod and 600Ft of redundant 2 inch gas pipe. They could b***** off if they thought they were using my earth nest.

Reply
  • Former Community Member
    0 Former Community Member
    I refused to have a PME supply when it was offered. My supply was OH TT, the earth electrode was a rod and 600Ft of redundant 2 inch gas pipe. They could b***** off if they thought they were using my earth nest.