The last remaining domestic circuits without RCD protection.

I prepared an EICR this morning for a two bed flat.


The peak installation has a 30 mA RCD main switch, which surprisingly despite being more than ten years old is a type A, so no RCD issues there.


The off-peak supplies two storage heater circuits run in surface mounted plastic mini trunking without RCD protection, so again no RCD issues. If I were installing the storage heaters with new circuits I would install RCD protection, but there’s no reason to condemn an existing installation.


I am just pondering exactly what can be installed in a domestic installation now without any RCD protection with the 18th Edition of the Wiring Regulations making them a requirement on lighting circuits there cannot be much left on the list.


 Andy B.
Parents
  • 100mA Type S feeding SWA then 30mA circuit(s) at end?

    In which case yes RCD protection of submain albeit not 30mA
Reply
  • 100mA Type S feeding SWA then 30mA circuit(s) at end?

    In which case yes RCD protection of submain albeit not 30mA