I prepared an EICR this morning for a two bed flat.


The peak installation has a 30 mA RCD main switch, which surprisingly despite being more than ten years old is a type A, so no RCD issues there.


The off-peak supplies two storage heater circuits run in surface mounted plastic mini trunking without RCD protection, so again no RCD issues. If I were installing the storage heaters with new circuits I would install RCD protection, but there’s no reason to condemn an existing installation.


I am just pondering exactly what can be installed in a domestic installation now without any RCD protection with the 18th Edition of the Wiring Regulations making them a requirement on lighting circuits there cannot be much left on the list.


 Andy B.
Parents
  •  



    However if you TT the detached garage is that an option?





    yes, provided you maintain double/reinforced insulation within the garage up to and including the first line RCD (good use for left-over plastic CUs perhaps? )


      - Andy.
Reply
  •  



    However if you TT the detached garage is that an option?





    yes, provided you maintain double/reinforced insulation within the garage up to and including the first line RCD (good use for left-over plastic CUs perhaps? )


      - Andy.