Are you all organised and have a supply of the new certificates to hand?
What do you actually think of them?
Andy B.
Andrew Jewsbury:
- TT system, the disconnection time of 0.2 s might not be achieved at IΔn and therefore the disconnection time should to relate to 5IΔn (if, as per the Note to 643.7.1 states, we take into account the operating characteristics of the device per Table 3A in Appendix 3) - that is unless your tester has a 2IΔn setting
On the other hand it would be rather odd to specify a test that couldn't necessarily physically be performed in a compliant installation. For a 30mA RCD, BS 7671 specifies a max Zs of 1667 Ohms (table 41.5) (or thereabouts - actually is is permitted to be higher provided RA doesn't exceed that figure (but I'll ignore that for the moment), the 200Ω figure is only a suggestion) - thus the maximum earth fault current we can really rely on is 230V/1667Ω = 138mA - i.e. below the 150mA needed for a 5x test. (Or if the tester has some means of generating the extra current, the touch voltage would exceed 50V which would likely abort the test anyway).
I guess this is all a results of the discussion about removing RCD testing from the 18th - it does seem peculiar though to record the result of a test if you're not recording an indication of which test was performed.
- Andy.
Andrew Jewsbury:
- TT system, the disconnection time of 0.2 s might not be achieved at IΔn and therefore the disconnection time should to relate to 5IΔn (if, as per the Note to 643.7.1 states, we take into account the operating characteristics of the device per Table 3A in Appendix 3) - that is unless your tester has a 2IΔn setting
On the other hand it would be rather odd to specify a test that couldn't necessarily physically be performed in a compliant installation. For a 30mA RCD, BS 7671 specifies a max Zs of 1667 Ohms (table 41.5) (or thereabouts - actually is is permitted to be higher provided RA doesn't exceed that figure (but I'll ignore that for the moment), the 200Ω figure is only a suggestion) - thus the maximum earth fault current we can really rely on is 230V/1667Ω = 138mA - i.e. below the 150mA needed for a 5x test. (Or if the tester has some means of generating the extra current, the touch voltage would exceed 50V which would likely abort the test anyway).
I guess this is all a results of the discussion about removing RCD testing from the 18th - it does seem peculiar though to record the result of a test if you're not recording an indication of which test was performed.
- Andy.