30 mA |
Conduct both 1x and 5x tests. Requires loop impedance less than 1364 Ω if you take into account full volt drop Record the 5x result. Verifies both additional protection to 643.7 and ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. Whilst the full Zs of 1667 Ω presented in Table 41.5 wouldn't provide sufficient current for a 5x test with lower voltages, earth electrode resistance should be limited to 200 Ω so no issues anticipated |
30 mA |
Conduct both 1x and 5x tests. Requires loop impedance less than 1364 Ω if you take into account full volt drop Record the 5x result. Verifies both additional protection to 643.7 and ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. Whilst the full Zs of 1667 Ω presented in Table 41.5 wouldn't provide sufficient current for a 5x test with lower voltages, earth electrode resistance should be limited to 200 Ω so no issues anticipated |