If an RCD does not trip at 1 x Idelta n then it is defective. This softer test is a better indicator of RCD health than the 5 x test and consumer safety.
This does not unfortunately take account of a small number of cases where the RCD passes a 1x test, but then goes on to fail a 5x test, although I agree this is not simply a case of "sticky RCD".
In fact, I am undecided in some cases whether this phenomenon is a combination of other external influence and/or a property of how a particular test set operates under given conditions.
Having said that I have seen this behavior on devices with different test sets at the same time doesn't help, as an influence on the supply might well have caused the problem, and of course we know of cases where RCDs returned to manufacturers having "failed" on-site have been tested in isolation and found to be operating perfectly well.
But that in itself causes another question regarding RCDs used for Additional Protection, or fault protection where 0.2 s disconnection time is required ... i.e. will they actually operated as expected?
Andrew Jewsbury:
I've definitely seen RCDs with longer trip times at 5IΔn than at IΔn, so IΔn is not always the "worst case" either!
In which case, can we have any confidence that a 1x (or 5x) test will give realistic assurance that the RCD will open in the required time when subject to a real earth fault - which could be many amps in magnitude?
Most RCD testers do not test at 2IΔn, and therefore the only option is 5IΔn.
Cue for a new range of "18th Ed" RCD testers with a 2x option?
Perhaps more practically we should only be thinking in terms of 'sampling' the RCDs performance at a few points and if they're within spec then say it's reasonable to assume that the RCD is functioning as designed and so will operate within specification throughout its entire range. Perhaps single test (1x perhaps) would be sufficient. I gather that some manufacturers suggested that operating the T button and observing an 'immediate' trip could be sufficient.
These require RCDs for Additional Protection - in this case this would invoke the 5IΔn test. To add all these requirements together, we have a maximum loop impedance for a 30 mA RCD of 230*.95/0.15 Ω (where additional protection is needed), i.e. 1457 Ω and not 1667 Ω
Humm - not sure of the logic there - additional protection is usually aimed at situations of direct contact (nails through cables, flexes cut by lawnmowers, touching the contacts of lampholders) - where the c.p.c. and hence Zs aren't usually of relevance (likewise any calculations involving Uo or Cmin). In a functioning installation we're only really worried about 150mA going through the victim's body, where it goes after that isn't a concern. Certainly for a successful test we'd need a lowish loop impedance, but that requirement doesn't seem to be obviously written into BS 7671.
Would you think it acceptable to perform a 5x test by placing the tester's earth probe on the supply N rather than PE? That would avoid problems due to a high Zs but still test the RCD's fundamental operation?
I've definitely seen RCDs with longer trip times at 5IΔn than at IΔn, so IΔn is not always the "worst case" either!
Most RCD testers do not test at 2IΔn, and therefore the only option is 5IΔn.
These require RCDs for Additional Protection - in this case this would invoke the 5IΔn test. To add all these requirements together, we have a maximum loop impedance for a 30 mA RCD of 230*.95/0.15 Ω (where additional protection is needed), i.e. 1457 Ω and not 1667 Ω
Andrew Jewsbury:
- TT system, the disconnection time of 0.2 s might not be achieved at IΔn and therefore the disconnection time should to relate to 5IΔn (if, as per the Note to 643.7.1 states, we take into account the operating characteristics of the device per Table 3A in Appendix 3) - that is unless your tester has a 2IΔn setting
On the other hand it would be rather odd to specify a test that couldn't necessarily physically be performed in a compliant installation. For a 30mA RCD, BS 7671 specifies a max Zs of 1667 Ohms (table 41.5) (or thereabouts - actually is is permitted to be higher provided RA doesn't exceed that figure (but I'll ignore that for the moment), the 200Ω figure is only a suggestion) - thus the maximum earth fault current we can really rely on is 230V/1667Ω = 138mA - i.e. below the 150mA needed for a 5x test. (Or if the tester has some means of generating the extra current, the touch voltage would exceed 50V which would likely abort the test anyway).
I guess this is all a results of the discussion about removing RCD testing from the 18th - it does seem peculiar though to record the result of a test if you're not recording an indication of which test was performed.
- Andy.
- TT system, the disconnection time of 0.2 s might not be achieved at IΔn and therefore the disconnection time should to relate to 5IΔn (if, as per the Note to 643.7.1 states, we take into account the operating characteristics of the device per Table 3A in Appendix 3) - that is unless your tester has a 2IΔn setting