Interlocked sockets

Hi all.


Recently had a contractor carry out a periodic inspection on our site (warehousing and workshops) and they have specified that all the 16A and 32A (1ph & 3ph) sockets need to be interlocked.


Is this true, or are they just finding £5k of additional work to carry out?


I can only find reference to caravan sites (Sec. 708) requiring interlocked sockets. 


Any other sections that reference this requirement on industrial and commercial installations?


Thanks in advance,

Neil

Parents
  • I can think of no reason why these should be interlocked from the Regs. This sounds like the inspector needs some proper training! The interlocked requirement only applies to certain special locations.
Reply
  • I can think of no reason why these should be interlocked from the Regs. This sounds like the inspector needs some proper training! The interlocked requirement only applies to certain special locations.