BS 7671 interpretation of clause 560.7.7

Within BS7671 there is the following clause:-

560.7.7 Safety circuit cables, other than metallic screened, fire-resistant cables, shall be adequately and reliably separated by distance or by barriers from other circuit cables, including other safety circuit cables.

Now I read this in two ways, the first is this is specifically talking about fire rated cables only… or

This is insinuating that unless I use a metallic screened fire-resistant cable I must provide separation by distance or by barriers including from other safety circuit cables. Does this mean a common dedicated medical IT final circuit trunking is not acceptable as each IT circuit in its own right is a safety circuit, therefore if I was to move away from fire rated cable I would need to ensure each IT circuit is installed in its own individual piece of containment (conduit) to give the correct level of separation or would a common galvanised trunking dedicated to the IT cabling be sufficient.

I appreciate no one will give me an answer to the question above, but can people let me know how they interpret this clause to see if I’m on the right lines.  

Can I ask how do you interpret this clause?

Parents
  • Interesting answer Alasdair the only with this is in HTM 06-01 it states all IT final circuits should be classed as safety circuits and clause 560.7.7 starts by saying safety circuits cables not safety service cable. So it’s hard to ignore this could include IT systems cabling. Also if you read 560.1 the examples of safety services include - Essential Medical systems 
     

    Graham, in regards to your post, it’s difficult to do that as the remaining section of 560.7 talks about safety services so would fall in line with Alasdair point, however 560.7.7 actually states the wording safety circuits which is stated in the HTM



Reply
  • Interesting answer Alasdair the only with this is in HTM 06-01 it states all IT final circuits should be classed as safety circuits and clause 560.7.7 starts by saying safety circuits cables not safety service cable. So it’s hard to ignore this could include IT systems cabling. Also if you read 560.1 the examples of safety services include - Essential Medical systems 
     

    Graham, in regards to your post, it’s difficult to do that as the remaining section of 560.7 talks about safety services so would fall in line with Alasdair point, however 560.7.7 actually states the wording safety circuits which is stated in the HTM