Double wound safety transformer for EV supply.

Hi everyone, I have only posted once before so thanks to anyone who replies!


I am following on from the earlier "70 volt PEN conductor not allowed to exceed post", and looking into supplying a client with an electric vehicle power supply from a three phase isolating transformer BS 7671 722.413 (1.2): " The circuit shall be supplied through a fixed isolating transformer.."


The general consensus seems to be that an external IP box with an RCD (Type B) and a tethered lead is the standard to follow, and this may be the only option with a 230 volt domestic supply, but why not use a 3 phase 400 volt step down or tapped, safety double wound isolation transformer in a standard 100 -200 ampere or above industrial units/sheds?

( Subject to load and diversity).


The answer often stated when I have asked sparks/engineers is that in-rush current are too high but a type D CB BS 60898 will 'let through' the in-rush ( the transformer manufacturer agrees), and will still give at 5 seconds- (final circuit exceeding 32 A) 0.44 ohm EL ( 10oC) , so is achievable in many situations local to Birmingham.


I was then going to run a fused cable out to an external isolated IP 65 box with a Type 2 socket to IP44 or above ( 722.55.101).


Isn't it better to engineer a solution to the upcoming electric charger deluge, rather than buying (insert well known manufacturer name here), and lots of single phase loads usually dumped onto L1?


I would be interested in any thoughts or problems you may consider....





Parents

  • davezawadi:

    Andy

    In the separated system there is no danger from a charging live to chassis fault, unless there is also some way of accessing the neutral as well, which is connected to the PE connection and with my suggested arrangement will immediately trip the RCD. Remember nothing on the secondary side of the isolating transformer is connected to real earth, nor any Protective Earth connection. Moving to the block diagram, there is complete isolation between the charging supply and the charger output which is illustrated by the dotted line. This is the exact point at which double insulation may be applied, and would be conventionally done so in a normal class 2 power supply unit. If signalling is required along the earth wire (presumably the earth neutral loop), it also needs class 2 isolation but this is not beyond the wit of man to design. A worldwide standard needs to match all possible systems in use, it would be reasonable to have a list of who suggested what (daft) idea, and who voted it through!


    I am almost disgusted by Graham's comment that "its in product standard" or words to that effect, because a faulty product standard is no excuse to continue to use it, for example cladding for buildings!! The job of the standards committee is to produce proper and safe standards, and this should be completely isolated from any manufacturer or other political pressure. This also does not appear to be the case with BS7671. I have sat on standardisation committees in the past and a major issue has always been from manufacturers who are not prepared to change their own ideas, although they send often unskilled persons as representatives. A manufacturer trying to save tiny amounts of money in the design of the car is foolish beyond words, the reliability and safety of the car must be considered first, as both are the way reputations can be lost very quickly.




    If what you say is correct, then are you proposing BS 7671 prohibit EV charging equipment to current standards, which don't include an isolating transformer - or to PME systems in particular?


    Caravans and mobile/transportable units are also prohibited from connection to PME systems - does that make those "defective products" - definitely not! Also, doesn't stop homeowners plugging their caravans into their PME homes for many months of the year.


    There are definitely issues with isolating transformers in EV charging equipment - in particular, might effectively mean a CU change on occasion. In Engineering, there is often no "right answer".


    The situation with EV charging isn't unique with respect to differences between product standards and good installation practice [in a particular nation or region].

Reply

  • davezawadi:

    Andy

    In the separated system there is no danger from a charging live to chassis fault, unless there is also some way of accessing the neutral as well, which is connected to the PE connection and with my suggested arrangement will immediately trip the RCD. Remember nothing on the secondary side of the isolating transformer is connected to real earth, nor any Protective Earth connection. Moving to the block diagram, there is complete isolation between the charging supply and the charger output which is illustrated by the dotted line. This is the exact point at which double insulation may be applied, and would be conventionally done so in a normal class 2 power supply unit. If signalling is required along the earth wire (presumably the earth neutral loop), it also needs class 2 isolation but this is not beyond the wit of man to design. A worldwide standard needs to match all possible systems in use, it would be reasonable to have a list of who suggested what (daft) idea, and who voted it through!


    I am almost disgusted by Graham's comment that "its in product standard" or words to that effect, because a faulty product standard is no excuse to continue to use it, for example cladding for buildings!! The job of the standards committee is to produce proper and safe standards, and this should be completely isolated from any manufacturer or other political pressure. This also does not appear to be the case with BS7671. I have sat on standardisation committees in the past and a major issue has always been from manufacturers who are not prepared to change their own ideas, although they send often unskilled persons as representatives. A manufacturer trying to save tiny amounts of money in the design of the car is foolish beyond words, the reliability and safety of the car must be considered first, as both are the way reputations can be lost very quickly.




    If what you say is correct, then are you proposing BS 7671 prohibit EV charging equipment to current standards, which don't include an isolating transformer - or to PME systems in particular?


    Caravans and mobile/transportable units are also prohibited from connection to PME systems - does that make those "defective products" - definitely not! Also, doesn't stop homeowners plugging their caravans into their PME homes for many months of the year.


    There are definitely issues with isolating transformers in EV charging equipment - in particular, might effectively mean a CU change on occasion. In Engineering, there is often no "right answer".


    The situation with EV charging isn't unique with respect to differences between product standards and good installation practice [in a particular nation or region].