Double wound safety transformer for EV supply.

Hi everyone, I have only posted once before so thanks to anyone who replies!


I am following on from the earlier "70 volt PEN conductor not allowed to exceed post", and looking into supplying a client with an electric vehicle power supply from a three phase isolating transformer BS 7671 722.413 (1.2): " The circuit shall be supplied through a fixed isolating transformer.."


The general consensus seems to be that an external IP box with an RCD (Type B) and a tethered lead is the standard to follow, and this may be the only option with a 230 volt domestic supply, but why not use a 3 phase 400 volt step down or tapped, safety double wound isolation transformer in a standard 100 -200 ampere or above industrial units/sheds?

( Subject to load and diversity).


The answer often stated when I have asked sparks/engineers is that in-rush current are too high but a type D CB BS 60898 will 'let through' the in-rush ( the transformer manufacturer agrees), and will still give at 5 seconds- (final circuit exceeding 32 A) 0.44 ohm EL ( 10oC) , so is achievable in many situations local to Birmingham.


I was then going to run a fused cable out to an external isolated IP 65 box with a Type 2 socket to IP44 or above ( 722.55.101).


Isn't it better to engineer a solution to the upcoming electric charger deluge, rather than buying (insert well known manufacturer name here), and lots of single phase loads usually dumped onto L1?


I would be interested in any thoughts or problems you may consider....





Parents
  • Thanks for the reply and information Mike.


    The resistor getting hot won't be an issue as it could be mounted in the transformer enclosure, I would just need to ensure good ventilation for both.


    I can mention this if we order with the manufacturer and see if they can size up allowing for this and some ceramic connectors as well.


    Re: Contactors and staging/staggering the start up's. we could just put delay timers onto the contactors and perhaps even incorporate a stop circuit as well as isolation.


    Thanks  for your comments


    Simon.
Reply
  • Thanks for the reply and information Mike.


    The resistor getting hot won't be an issue as it could be mounted in the transformer enclosure, I would just need to ensure good ventilation for both.


    I can mention this if we order with the manufacturer and see if they can size up allowing for this and some ceramic connectors as well.


    Re: Contactors and staging/staggering the start up's. we could just put delay timers onto the contactors and perhaps even incorporate a stop circuit as well as isolation.


    Thanks  for your comments


    Simon.