Double wound safety transformer for EV supply.

Hi everyone, I have only posted once before so thanks to anyone who replies!


I am following on from the earlier "70 volt PEN conductor not allowed to exceed post", and looking into supplying a client with an electric vehicle power supply from a three phase isolating transformer BS 7671 722.413 (1.2): " The circuit shall be supplied through a fixed isolating transformer.."


The general consensus seems to be that an external IP box with an RCD (Type B) and a tethered lead is the standard to follow, and this may be the only option with a 230 volt domestic supply, but why not use a 3 phase 400 volt step down or tapped, safety double wound isolation transformer in a standard 100 -200 ampere or above industrial units/sheds?

( Subject to load and diversity).


The answer often stated when I have asked sparks/engineers is that in-rush current are too high but a type D CB BS 60898 will 'let through' the in-rush ( the transformer manufacturer agrees), and will still give at 5 seconds- (final circuit exceeding 32 A) 0.44 ohm EL ( 10oC) , so is achievable in many situations local to Birmingham.


I was then going to run a fused cable out to an external isolated IP 65 box with a Type 2 socket to IP44 or above ( 722.55.101).


Isn't it better to engineer a solution to the upcoming electric charger deluge, rather than buying (insert well known manufacturer name here), and lots of single phase loads usually dumped onto L1?


I would be interested in any thoughts or problems you may consider....





Parents
  • The use of a safety isolating transformer to provide an isolated supply seems to be being criticised here as unsafe in some way. An isolating transformer construction prevents any significant secondary voltage to any part of the primary circuit by class 2 insulation and an earthed screen between windings, so I cannot understand Andy's comment about capacitive coupling. An RCD on the secondary allows the neutral before the RCD to be connected to the earth connection of the car, as the only potentially dangerous scenario would be contact with both the car body and the cable live conductor, or an earth fault between the cable live and real earth AND contact from the car to earth by a person or livestock.  Both of these would trip the RCD, and must be considered as safe as any other equipment outdoors. A broken CNE would not be dangerous as far as the car is concerned, but could be at any other point in the installation where the installation earth and real Earth could both be contacted, although in theory this should not happen. Of course contacting BOTH live conductors in the charge cable would be just as dangerous as anywhere else.


    I have commented a number of times on the design error of cars, they should be class 2 and then all these problems go away at very low cost. I am also somewhat dismayed that a DC tripping RCD is needed for AC mains charge supplies as I see no way that a DC danger could occur, at least not if the batteries are isolated from the charge supply. None of the suggested supply arrangements are safe with PME supplies where the neutral is not to be trusted, and the COP is a pretty bad job in many domestic circumstances, where the car may be charged in or close to a garage with significant metalwork connected to the PME earth.

Reply
  • The use of a safety isolating transformer to provide an isolated supply seems to be being criticised here as unsafe in some way. An isolating transformer construction prevents any significant secondary voltage to any part of the primary circuit by class 2 insulation and an earthed screen between windings, so I cannot understand Andy's comment about capacitive coupling. An RCD on the secondary allows the neutral before the RCD to be connected to the earth connection of the car, as the only potentially dangerous scenario would be contact with both the car body and the cable live conductor, or an earth fault between the cable live and real earth AND contact from the car to earth by a person or livestock.  Both of these would trip the RCD, and must be considered as safe as any other equipment outdoors. A broken CNE would not be dangerous as far as the car is concerned, but could be at any other point in the installation where the installation earth and real Earth could both be contacted, although in theory this should not happen. Of course contacting BOTH live conductors in the charge cable would be just as dangerous as anywhere else.


    I have commented a number of times on the design error of cars, they should be class 2 and then all these problems go away at very low cost. I am also somewhat dismayed that a DC tripping RCD is needed for AC mains charge supplies as I see no way that a DC danger could occur, at least not if the batteries are isolated from the charge supply. None of the suggested supply arrangements are safe with PME supplies where the neutral is not to be trusted, and the COP is a pretty bad job in many domestic circumstances, where the car may be charged in or close to a garage with significant metalwork connected to the PME earth.