gkenyon:
SL1:
gkenyon:
The situation that does arise, however, is high inrush current of the rather sizeable transformers. Yes, this can be overcome, but of course costs are now increasing, and we're competing against "forget it, I'll just plug it in to a socket-outlet", which of course is far less practical, and far less safe, but doesn't have the price tag attached.
Just a thought on this ... Regulation 722.411.4.1 provides other options for three-phase installations. However, I guess such an approach would not be precluded, provided the requisite RCDs are used as indicated in the IET Code of Practice and to meet the requirements of section 722 of BS 7671.
Thanks for you comments.
However, isn't it the case that if you follow Section 722.413.1.2, and use a Safety double insulated transformer Section 413 Electrical separation is in use.
Therefore would the additional RCD's be required and isn't the RCD built into the manufacturers lead sufficient anyway? Surely a risk assessment could easily acknowledge that the separation system used, along with the manufacturers vehicle building-in RCD with purpose built lead and Type of socket.
The point of the exercise was to use the transformer protective measure rather than have the RCD so adding in the RCD on top would then defeat the idea of needing the protective separation measure, and introduce the CEN PME 70 volt rms etc problems.
Isn't it an either/ or situation offered by Section 722?
Regards
Simon
gkenyon:
SL1:
gkenyon:
The situation that does arise, however, is high inrush current of the rather sizeable transformers. Yes, this can be overcome, but of course costs are now increasing, and we're competing against "forget it, I'll just plug it in to a socket-outlet", which of course is far less practical, and far less safe, but doesn't have the price tag attached.
Just a thought on this ... Regulation 722.411.4.1 provides other options for three-phase installations. However, I guess such an approach would not be precluded, provided the requisite RCDs are used as indicated in the IET Code of Practice and to meet the requirements of section 722 of BS 7671.
Thanks for you comments.
However, isn't it the case that if you follow Section 722.413.1.2, and use a Safety double insulated transformer Section 413 Electrical separation is in use.
Therefore would the additional RCD's be required and isn't the RCD built into the manufacturers lead sufficient anyway? Surely a risk assessment could easily acknowledge that the separation system used, along with the manufacturers vehicle building-in RCD with purpose built lead and Type of socket.
The point of the exercise was to use the transformer protective measure rather than have the RCD so adding in the RCD on top would then defeat the idea of needing the protective separation measure, and introduce the CEN PME 70 volt rms etc problems.
Isn't it an either/ or situation offered by Section 722?
Regards
Simon