Double wound safety transformer for EV supply.
Hi everyone, I have only posted once before so thanks to anyone who replies!
I am following on from the earlier "70 volt PEN conductor not allowed to exceed post", and looking into supplying a client with an electric vehicle power supply from a three phase isolating transformer BS 7671 722.413 (1.2): " The circuit shall be supplied through a fixed isolating transformer.."
The general consensus seems to be that an external IP box with an RCD (Type B) and a tethered lead is the standard to follow, and this may be the only option with a 230 volt domestic supply, but why not use a 3 phase 400 volt step down or tapped, safety double wound isolation transformer in a standard 100 -200 ampere or above industrial units/sheds?
( Subject to load and diversity).
The answer often stated when I have asked sparks/engineers is that in-rush current are too high but a type D CB BS 60898 will 'let through' the in-rush ( the transformer manufacturer agrees), and will still give at 5 seconds- (final circuit exceeding 32 A) 0.44 ohm EL ( 10oC) , so is achievable in many situations local to Birmingham.
I was then going to run a fused cable out to an external isolated IP 65 box with a Type 2 socket to IP44 or above ( 722.55.101).
Isn't it better to engineer a solution to the upcoming electric charger deluge, rather than buying (insert well known manufacturer name here), and lots of single phase loads usually dumped onto L1?
I would be interested in any thoughts or problems you may consider....
Parents
  • CliveS:
    Could one of you please draw a circuit diagram showing the electric car and battery and voltage, the DC leads; the main transformer/supply, diodes and protection fuses or circuit beakers with earthing lead arrangement so that we can all understand what is required to construct a vehicle charging station safely.  Please avoid using and initials like PME, YY or CPC  unless their are defined in words. Thank you.
    The term "PME" and "CPC" are standard terms in BS 7671. "YY" is a cable type, and appears in the On-Site Guide.
    These are all standard terms !
Reply
  • CliveS:
Children
No Data