Purely from an electrician's point of view, a P.M.E. supply to a radio shack that has earthed equipment with conductive parts such as earthed cases that can be touched can present shock risks. The P.M.E. earth is connected directly to the neutral of the supply cable at the main intake meter position in the house. The neutral can attain a Voltage above true earth, as the neutral carries current and supply conductor cables' resistance cause a Voltage rise on the neutral. So, a P.M.E. earth terminal in the house can attain a Voltage above true earth, and this Voltage can appear on earthed equipment in the radio shack.
If you have conductive parts in the shack that are earthed via an earth rod at the shack, there can be a Voltage appearing between TT earthed equipment and P.M.E. earthed equipment. This is undesirable, and could be dangerous.
Purely from an electrician's point of view, a P.M.E. supply to a radio shack that has earthed equipment with conductive parts such as earthed cases that can be touched can present shock risks. The P.M.E. earth is connected directly to the neutral of the supply cable at the main intake meter position in the house. The neutral can attain a Voltage above true earth, as the neutral carries current and supply conductor cables' resistance cause a Voltage rise on the neutral. So, a P.M.E. earth terminal in the house can attain a Voltage above true earth, and this Voltage can appear on earthed equipment in the radio shack.
If you have conductive parts in the shack that are earthed via an earth rod at the shack, there can be a Voltage appearing between TT earthed equipment and P.M.E. earthed equipment. This is undesirable, and could be dangerous.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site