Sizing cable for forklift

Former Community Member
Former Community Member
Hi all, charger plate has following info;

230vac single phase

Rated at 44amps


Cable length will be 5 meters and method to be clip direct. 


I'm thinking of using a 45amp rcbo, and a 4mm swa which gives me 49amps if clipped direct. 


The thing that's putting me off is that the charger comes with a pre installed tail which looks like a 10 mm conductor size have I missed something here?


Regards TS
attachments.zip
Parents
  • Former Community Member
    0 Former Community Member
    Thanks for pointing out the round flex table this now makes alot more sense, I'm assuming that I should select a type C mcb for this too incase of inrush current as I have no experience in this and am unable to get hold of the manufacturer for guidance. 


    Regards TS
Reply
  • Former Community Member
    0 Former Community Member
    Thanks for pointing out the round flex table this now makes alot more sense, I'm assuming that I should select a type C mcb for this too incase of inrush current as I have no experience in this and am unable to get hold of the manufacturer for guidance. 


    Regards TS