In the Deopke paper, the chart near the top of page 11 says that Type A RCDs are not suitable for heat pump applications,
to consumer unit - front-end 30ma Type A/C RCD main switch.
My thinking is that a Type A\\C won't be affected if the feed to the pump RCD/Type C mcb is taken off the incoming side of the Type A/C - i.e. in connected in parallel.
Ah, so the AC RCD isn't the main incomer then - more of a split load arrangement (in which case a switch disconnector as the incomer might be appropriate - rather than messing about with labels to try and explain that what looks like in incoming devices doesn't in fact isolate all the outgoing circuits).
Might be simpler (and provide better discrimination) to use DP switching RCBOs for the other outgoing circuits and then an MCB plus suitable RCCB for the heat pump (presuming the type of RCD needed for the heat pump isn't available as an RCBO).
- Andy.
In the Deopke paper, the chart near the top of page 11 says that Type A RCDs are not suitable for heat pump applications,
to consumer unit - front-end 30ma Type A/C RCD main switch.
My thinking is that a Type A\\C won't be affected if the feed to the pump RCD/Type C mcb is taken off the incoming side of the Type A/C - i.e. in connected in parallel.
Ah, so the AC RCD isn't the main incomer then - more of a split load arrangement (in which case a switch disconnector as the incomer might be appropriate - rather than messing about with labels to try and explain that what looks like in incoming devices doesn't in fact isolate all the outgoing circuits).
Might be simpler (and provide better discrimination) to use DP switching RCBOs for the other outgoing circuits and then an MCB plus suitable RCCB for the heat pump (presuming the type of RCD needed for the heat pump isn't available as an RCBO).
- Andy.