interpretation of SPD para in GN1 (18th)

"It should be noted that SPD's required by Section 443 of BS 7671 are to protect the electrical power installation, but exclude any electronic equipment, the protection of which is outside the scope of BS 7671."


what does that break down to mean ?


- that SPD's are for the (im interpretting 'electrical power installation' here to be...) fixed installation and any thing not permanently connected, is excluded ?

- that SPD's are for the fixed installation and any thing connected (permanently or otherwise) is included, *except* electronic equipment (which is pretty much every thing these days) ?

- that SPD's are for the fixed intallation and any thing connected is included, but what is the last bit re: electronic equipment about ?

- something else ?


Initially I went for the first of the above, but the definition of electrical equipment is clear enough, so what is that para getting at.


Hmmm

Habs
Parents

  • Whilst perhaps not well worded, telecomms and similar systems ('ICT systems') are specifically excluded from the scope of Section 443 of  BS 7671, as it is covered sufficiently well in other standards.



    But surely there are loads of electronics that aren't anything to do with ICT systems - everything from RCBOs to dimmer switches to electronic "transformers" for SELV lighting to variable speed drives for motors.


      - Andy.
Reply

  • Whilst perhaps not well worded, telecomms and similar systems ('ICT systems') are specifically excluded from the scope of Section 443 of  BS 7671, as it is covered sufficiently well in other standards.



    But surely there are loads of electronics that aren't anything to do with ICT systems - everything from RCBOs to dimmer switches to electronic "transformers" for SELV lighting to variable speed drives for motors.


      - Andy.