The EMC requirements for RCDs have become more onerous over time. Whilst an RCD say 10 years old might be expected to deal with frequencies of 2.4 GHz, say, that wasn't necessarily the case 20 years ago.
However, installation of an RCD close to [almost adjacent to] a source of disturbances without mitigation (metallic enclosure) would not necessarily comply with BS 7671 requirements for EMC. Whilst the use of metal consumer units helps avoid problems for electronic components in the consumer unit, it can also adversely affect the wireless signal of the smart meter, as can all of the copper within the consumer unit anyway.
To be honest, not well thought-through at all if the wireless adaptor is too close to the consumer unit or concentrations of wiring. Separation distance of at least 100 mm are recommended.
The EMC requirements for RCDs have become more onerous over time. Whilst an RCD say 10 years old might be expected to deal with frequencies of 2.4 GHz, say, that wasn't necessarily the case 20 years ago.
However, installation of an RCD close to [almost adjacent to] a source of disturbances without mitigation (metallic enclosure) would not necessarily comply with BS 7671 requirements for EMC. Whilst the use of metal consumer units helps avoid problems for electronic components in the consumer unit, it can also adversely affect the wireless signal of the smart meter, as can all of the copper within the consumer unit anyway.
To be honest, not well thought-through at all if the wireless adaptor is too close to the consumer unit or concentrations of wiring. Separation distance of at least 100 mm are recommended.