Tripping RCD after smart meter install

I got called to a property today. The RCD had started tripping after a smart meter was installed. The insulation resistance between line and cpc was over 300 Mohm on all circuits. The RCD was an MEM unit in a memera 2000 consumer unit.


Whilst at the property the RCD did not trip. I did a google search and one result suggested the RF from the smart meters transceiver was upsetting the RCD. When the smart meter was first energised I guess it starts communicating with the supplier causing said RF.


We have had 3 properties now all with MEM RCD's which have started tripping after smart meters have been installed, normally in the early hours of the day.


Just wondering if anyone else has experienced of this issue?
Parents
  • I was going to try a mobile near the RCD if I got called back. Accidentally the smart meters transceiver box did fall off the meter board whilst I was at the property, I tucked it up out as far as possible to get it away from the RCD. 


    PS I know the meter board and consumer unit are in a rubbish position behind the curtain....