Tripping RCD after smart meter install

I got called to a property today. The RCD had started tripping after a smart meter was installed. The insulation resistance between line and cpc was over 300 Mohm on all circuits. The RCD was an MEM unit in a memera 2000 consumer unit.


Whilst at the property the RCD did not trip. I did a google search and one result suggested the RF from the smart meters transceiver was upsetting the RCD. When the smart meter was first energised I guess it starts communicating with the supplier causing said RF.


We have had 3 properties now all with MEM RCD's which have started tripping after smart meters have been installed, normally in the early hours of the day.


Just wondering if anyone else has experienced of this issue?
Parents
  • I had a similar experience a month or so ago. 20 yo Crabtree RCD was tripping randomly at night, usually on a Monday night between

    midnight and 2am in the morning. Once reset, no trips for another week. I changed the RCD, it still happened.

    Eventually I changed the board for a metal clad RCBO board. No trips since. All testing was done beforehand, no fault anywhere.

    https://communities.theiet.org/discussions/viewtopic/1037/23887
Reply
  • I had a similar experience a month or so ago. 20 yo Crabtree RCD was tripping randomly at night, usually on a Monday night between

    midnight and 2am in the morning. Once reset, no trips for another week. I changed the RCD, it still happened.

    Eventually I changed the board for a metal clad RCBO board. No trips since. All testing was done beforehand, no fault anywhere.

    https://communities.theiet.org/discussions/viewtopic/1037/23887
Children
No Data