RCDs for both Fault & Additional Protection

BS7671 states for Additional Protection [415.1.2] - "The use of RCDs is not recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in Sections 411 to 414." - These methods being methods of protection against shock - ADS, Double Insulation, Separation & SELV/PELV.


531.3.6 states " - - - - - - -RCD - - --  - - -may provide fault protection and additional protection simultaneously."


This appears to be inconsistent. Is 531.3.6 meant to apply to only one type of neutral  earthing system?


Regards

Parents

  • but in some parts of the world such RCD and no earth installations are seen as OK - a sort of Class 0 + RCD.



    I can confirm that in some EU self catering type accommodation that is as good as it gets.....hob keeps tripping RCD.... no problem the resort will " fix it"  by disconnecting the CPC
Reply

  • but in some parts of the world such RCD and no earth installations are seen as OK - a sort of Class 0 + RCD.



    I can confirm that in some EU self catering type accommodation that is as good as it gets.....hob keeps tripping RCD.... no problem the resort will " fix it"  by disconnecting the CPC