RCDs for both Fault & Additional Protection

BS7671 states for Additional Protection [415.1.2] - "The use of RCDs is not recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in Sections 411 to 414." - These methods being methods of protection against shock - ADS, Double Insulation, Separation & SELV/PELV.


531.3.6 states " - - - - - - -RCD - - --  - - -may provide fault protection and additional protection simultaneously."


This appears to be inconsistent. Is 531.3.6 meant to apply to only one type of neutral  earthing system?


Regards

Parents
  • Isn't the point that


    415.1.2 implies that OPDs must be used and 


    531.3.6 states that that is not the case?

    I think PG is asking if this only applies to TT instalations.
Reply
  • Isn't the point that


    415.1.2 implies that OPDs must be used and 


    531.3.6 states that that is not the case?

    I think PG is asking if this only applies to TT instalations.