davezawadi:
and the supplementary bonding must be in place and tested (notice) before the equipment is energised.
Well, except for the potentially significant convenience of not having to turn the power off and verify exposed terminals are dead before unbolting things - as with signal cables, bonding can be removed and re-fitted, as soon as the jumbo mains plug is removed from the supply
As long as you're not importing protective conductor currents from elsewhere.
Yes you can have local isolation switches one per rack, but these in the heat of battle such things can be another source of accidentally switching off the wrong thing.
Same with plug and socket-outlet. They're all just isolators. And many racks will have two feeds (or more) - multiple points of isolation. In terms of accidentally switching off the wrong thing in the heat of the moment, let's also consider Regulation 12 of the Electricity at Work Regulations 1989 which definitely requires "... where appropriate, methods of identifying circuits ...": if it's operationally so important not to "flip the wrong switches", make sure they are properly identified, because this is required for safety in any case.
This does bring out a point from BS7671, which is the blanket requirement for RCDs for sockets up to 32A. In an installation such as this with supplementary bonding to earth, the RCD has exactly zero use!
Same with plug and socket-outlet. They're all just isolators.
AJJewsbury:
Same with plug and socket-outlet. They're all just isolators.
Sorry, but I've got to disagree with that. Plugs & sockets mean that IT technicians and change the power supply arrangements safely. Bare in mind that when something goes wrong with live (i.e. customer facing) systems in the IT world there is huge pressure on technicians to get things working as quickly as possible - calling in an electrician who might not turn up for a few hours simply isn't an option. Being able to unplug a rack from one supply and plug it into another nearby supply has saved things on my watch at least once.
- Andy.
Beard Weird:
This would have been an ideal topic to be forwarded to the IT section of the IET forum!
I think that Andy has also made an error worrying about direct contact with damaged cables etc by anyone. Whilst that could happen given enough various circumstances, realistically it is very very unlikely. I would point out that a single RCD for a rack of servers (which might take 100A of mains, probably 3x32A supply) would be foolish, the idea of fitting one each is worse! We have an electrical system which depends on proper earthing of exposed conductive parts, and automatic disconnection of supply by CPDs, yet this regulation is determined to fit even more unnecessary RCDs! The scope for RCD protection is way too wide, it should only be for sockets where portable appliances are likely to be used by unskilled persons, and the servers in a rack should be out of scope for portable appliances separately, as you need tools to make them portable