It would seem more that a little absurd that where a 32A BS EN 60309 wall mounted socket needs 30mA RCD protection, a wall mounted isolator with a stuffing gland supplying 6" of flex with a 32A BS EN 60309 female coupler on the end of it, in the same situation, would be exempted. (I note that the title of BS EN 60309 is "Plugs, socket-outlets and couplers..." so that's no help.)
IT cabinets are 3 Phase and I dread the thought of an IT Technician interconnecting the power to dual fed Servers for obvious reasons.
But this is precisely why I asked the specific question whether you were advocating 30 mA RCD protection for couplers as well!
In fact, I agree it's a difficult situation to grasp, but at the end of the day the Reg exists for "couplers" separate to "socket-outlets", and I can't see the difference between "appliance outlet" and "free outlet" in the context of a cable coupler.
So, the question - should couplers be included in 411.3.3 ? I sort of think you're saying they should be.
Bob C:
I have a situation where some of the IT cabinets are 3 Phase and I dread the thought of an IT Technician interconnecting the power to dual fed Servers for obvious reasons.
FCU -> Flex -> BS 1363 outlet (as in the pendant socket mentioned before, or a autorewind reel with a trailing socket on the end of the flex) - apparently a connector rather than a socket, so no RCD requirement?
I think this is a socket-outlet, or an accessory with socket-outlets, so I think 411.3.3 (i) applies.
AJJewsbury:
Bob C:
I have a Client that will not provide a Risk Assessment to omit an RCD Commando Socket for a Data Cabinet. He wishes to employ a local isolator for the Cabinet, however he is concerned that the PDU Strip that arrived on site from the factory and pre-fitted within the data cabinet would still need an RCD. It is my opinion that the Factory built Data Rack is classed as a piece of equipment and as such does not form part of the Contractor's installation. If the Rack had arrived on site without the PDU strip fitted and it was installed by the Contractor then this would form part of the installation and therefore would require an RCD. Any advice/assistance would be appreciated.Apologies for the apparent tangents - we're still debating the finer points.
So far we seem to agree that if the PDUs contain BS 1363 socket outlets then the 30mA RCD requirements would apply - so somehow or other that would need to be dealt with - either by a 30mA RCD in the supply circuit, or one or more 30mA RCDs within the PDU arrangement (or better still by risk assessment to eliminate the need for RCDs altogether - probably what most PDU manufacturers assume). Ditto if there are BS EN 60309 sockets (or even BS 546 sockets) rated 32A or less within the rack.
We seem to have mixed opinions still if other types of 'connectors' are used - e.g. the IEC 60320s chassis mount outlets often found on PDUs.
To me, trying to supply an IT rack without an risk assessment to omit 30mA RCDs is rather like trying to run a taxi service without a driving licence - while it's not impossible, the contortions you have to go through (hard wiring things that should be pluggable, perhaps needing 30mA RCDs when they're not really needed) make it a very dubious choice in the long run.
- Andy.
Bob C:
I have a Client that will not provide a Risk Assessment to omit an RCD Commando Socket for a Data Cabinet. He wishes to employ a local isolator for the Cabinet, however he is concerned that the PDU Strip that arrived on site from the factory and pre-fitted within the data cabinet would still need an RCD. It is my opinion that the Factory built Data Rack is classed as a piece of equipment and as such does not form part of the Contractor's installation. If the Rack had arrived on site without the PDU strip fitted and it was installed by the Contractor then this would form part of the installation and therefore would require an RCD. Any advice/assistance would be appreciated.
Apologies - not having access to BS EN 60320 I can't see the context of its definitions, so I'm having difficulty commenting on that bit. While I can see that the usual female IEC connector on the load end of a flex would certainly be a coupler (or "connector" in BS 7671 definition terms), I still can't see how the panel mount version (connected to "fixed" wiring and intended to accept a C14 plug on the supply end of the flex) would fit the same BS 7671 definitions. Looking at it the the way around, trailing 13A sockets come under BS 1363 - the standard for socket outlets, but surely in BS 7671 terms they're couplers/connectors, rather than socket outlets, when connected on the end of a flex rather than fixed wiring.
I do see your point about BS EN 60320 items not being listed as being acceptable socket types - but again that of itself doesn't say to me it's not a socket.
If I stuck a schuko socket on a wall, I think the usual conclusion would be that it was a departure from BS 7671 (which may or may not be justifiable under 133) rather than it needed to be given the name of a different kind of accessory.
So far we seem to be saying that, in the picture of the PDU above, that the right hand four "outlets" are sockets as far as BS 7671 is concerned, and so require 30mA RCD protection (unless a risk assessment concludes otherwise), but the eight "outlets" on the left, are deemed not to be socket outlets, so have no such requirements - even though they're likely to be used in exactly the same way. That's a conclusion I'm not entirely comfortable with.
13A Socket -> Plug -> Flex -> Appliance - OK (30mA RCD protection required at or before socket)
FCU -> Flex -> Appliance (might be fixed or hand-held) (no RCD requirement)
FCU -> Flex -> BS 1363 outlet (as in the pendant socket mentioned before, or a autorewind reel with a trailing socket on the end of the flex) - apparently a connector rather than a socket, so no RCD requirement?
FCU -> Flex -> BS EN 60320 connector - similarly, no RCD requirement?
FCU -> BS EN 60320 panel outlet (directly hard-wired, no flex) - not permitted?
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site