Hang on, that's picking at a single thing from a three-part reasoning.
AJJewsbury:
They are defined as "couplers" .... in Reg 553.2.1
Saying that couplers must comply with BS EN 60320 logically isn't the same as saying all things complying with BS EN 60320 must be couplers - that would be like saying since sockets must comply with BS 1363 then all things complying with BS 1363 must be called sockets - and thus you couldn't have a BS 1363 plug. (Or the classic example, since tables have four legs, all four legged things must be tables).
On a wider note, I'm getting less and less happy with the definition of a socket needing to be attached(?) to fixed wiring. There's no definition of fixed wiring (I could see that it could either be wiring that's not free to move, or equally, wiring that can't be readily unplugged from the supply and relocated). If following the example of 'fixed equipment' the former might be expected, but is there really a significant difference between a wall mounted socket and one of these? https://olsondirect.co.uk/4-way-13a-switched-socket-suspended-service-unit.html
- Andy.
They are defined as "couplers" .... in Reg 553.2.1
AJJewsbury:
No, not the couplers (e.g. on the end of a flex) - I mean the "chassis mount" outlets - often incorporated into rack mounted power distribution units (PDUs) in just the same way that BS 1363 outlets are. One example:
- Andy.
They are not socket-outlets no matter how common.
Are you advocating that RCDs are required for couplers now, as well as socket-outlets, and perhaps that the requirement should also be extended to connection units and connecting points too?
AJJewsbury:
In the UK, the consensus seems to be that general-purpose socket-outlets (BS 1363-2 and BS EN 60309-2) are exactly that ... general purpose, unless you have them locked away somewhere that's only accessible to suitably competent persons, for example ... hence the risk assessment requirement.
Same thinking for 60320 sockets? (C13 and C19s?) - pretty common in rack PDUs.
- Andy.
In the UK, the consensus seems to be that general-purpose socket-outlets (BS 1363-2 and BS EN 60309-2) are exactly that ... general purpose, unless you have them locked away somewhere that's only accessible to suitably competent persons, for example ... hence the risk assessment requirement.