RCD Protection at Data Cabinets
I have a Client that will not provide a Risk Assessment to omit an RCD Commando Socket for a Data Cabinet. He wishes to employ a local isolator for the Cabinet, however he is concerned that the PDU Strip that arrived on site from the factory and pre-fitted within the data cabinet would still need an RCD. It is my opinion that the Factory built Data Rack is classed as a piece of equipment and as such does not form part of the Contractor's installation. If the Rack had arrived on site without the PDU strip fitted and it was installed by the Contractor then this would form part of the installation and therefore would require an RCD. Any advice/assistance would be appreciated.
  • I'm not sure that the definition of "socket-outlet" in BS 7671 fully covers couplers, particularly as:
    • They are defined as "couplers" in BS EN 60320, and again in Reg 553.2.1.
    • BS EN 60320 appliance-outlets are not suitable for direct connection to the fixed wiring, they are part of equipment. Equipment should be selected in accordance with BS 7671 (i.e. meets relevant standards, suitable rating etc.)
    • BS EN 60320 is not listed in Table 55.1, as required by 553.1.3 unless 553.1.5 applies, and the use you are alluding to for data cabinets doesn't really come under any of the exceptions listed in 553.1.5 - so if you want to specify them, they cannot be "socket-outlets".
  • They are defined as "couplers" ....  in Reg 553.2.1
    Saying that couplers must comply with BS EN 60320 logically isn't the same as saying all things complying with BS EN 60320 must be couplers - that would be like saying since sockets must comply with BS 1363 then all things complying with BS 1363 must be called sockets - and thus you couldn't have a BS 1363 plug.  (Or the classic example, since tables have four legs, all four legged things must be tables).
    On a wider note, I'm getting less and less happy with the definition of a socket needing to be attached(?) to fixed wiring. There's no definition of fixed wiring (I could see that it could either be wiring that's not free to move, or equally, wiring that can't be readily unplugged from the supply and relocated). If following the example of 'fixed equipment' the former might be expected, but is there really a significant difference between a wall mounted socket and one of these? https://olsondirect.co.uk/4-way-13a-switched-socket-suspended-service-unit.html
  • AJJewsbury:
    Hang on, that's picking at a single thing from a three-part reasoning. Please don't take it out of context. 553.2.1 PLUS the fact that BS EN 60320 is "couplers" and the "outlets" are couplers as they comply with that standard.
    Having said that, you've not responded to the last point - you can't select them as socket-outlets, as that doesn't comply with BS 7671.
    No, and you're quite right.
    When the BS EN 60320 outlets are manufactured into a product and the whole product meets BS 5733, that product may be suitable for connection to the fixed wiring (as in the case of the BS 1363 version you point to).
    You can install an accessory to BS 5733 and connect it direct to fixed wiring, but if it has BS EN 60320 appliance outlet couplers, it will still have appliance couplers (rather than socket-outlets).
  • Hang on, that's picking at a single thing from a three-part reasoning.
    Apologies - not having access to BS EN 60320 I can't see the context of its definitions, so I'm having difficulty commenting on that bit. While I can see that the usual female IEC connector on the load end of a flex would certainly be a coupler (or "connector" in BS 7671 definition terms), I still can't see how the panel mount version (connected to "fixed" wiring and intended to accept a C14 plug on the supply end of the flex) would fit the same BS 7671 definitions. Looking at it the the way around, trailing 13A sockets come under BS 1363 - the standard for socket outlets, but surely in BS 7671 terms they're couplers/connectors, rather than socket outlets, when connected on the end of a flex rather than fixed wiring.
    I do see your point about BS EN 60320 items not being listed as being acceptable socket types - but again that of itself doesn't say to me it's not a socket. If I stuck a schuko socket on a wall, I think the usual conclusion would be that it was a departure from BS 7671 (which may or may not be justifiable under 133) rather than it needed to be given the name of a different kind of accessory. If push came to shove I might try and squeeze the use of 60320 "outlets" in under the last bit of 553.1.5 (iii) - 'necessary to distinguish the function of the circuit' (as it's function is to supply equipment that's supplied with IEC-IEC leads).
    So far we seem to be saying that, in the picture of the PDU above, that the right hand four "outlets" are sockets as far as BS 7671 is concerned, and so require 30mA RCD protection (unless a risk assessment concludes otherwise), but the eight "outlets" on the left, are deemed not to be socket outlets, so have no such requirements - even though they're likely to be used in exactly the same way. That's a conclusion I'm not entirely comfortable with.
    It also get really complicated with what are probably some common arrangements...
    13A Socket -> Plug -> Flex -> Appliance - OK (30mA RCD protection required at or before socket)
    FCU -> Flex -> Appliance (might be fixed or hand-held) (no RCD requirement)
    FCU -> Flex -> BS 1363 outlet (as in the pendant socket mentioned before, or a autorewind reel with a trailing socket on the end of the flex) - apparently a connector rather than a socket, so no RCD requirement?
    FCU -> Flex -> BS EN 60320 connector - similarly, no RCD requirement?
    FCU -> BS EN 60320 panel outlet (directly hard-wired, no flex) - not permitted?
    (and I suppose ditto without the FCU when supplied from a 20A or less circuit)
    It's all getting murkier and murkier....
  • Apologies - not having access to BS EN 60320 I can't see the context of its definitions, so I'm having difficulty commenting on that bit. While I can see that the usual female IEC connector on the load end of a flex would certainly be a coupler (or "connector" in BS 7671 definition terms), I still can't see how the panel mount version (connected to "fixed" wiring and intended to accept a C14 plug on the supply end of the flex) would fit the same BS 7671 definitions. Looking at it the the way around, trailing 13A sockets come under BS 1363 - the standard for socket outlets, but surely in BS 7671 terms they're couplers/connectors, rather than socket outlets, when connected on the end of a flex rather than fixed wiring.
    I think the title of the standard is sufficient.
    No, but it does mean you shouldn't really be specifying it if it is.
    But the standard for Shuko socket-outlets are "socket-outlets". But yes, might be acceptable for, say, a factory test area where export appliances are made, as it would be a safer option than using a UK or Industrial socket-outlet in that particular case, but in "domestic and similar" situations, the Plugs and Sockets (Safety) Regulations apply, plus the requirement for shuttered outlets in that type of usage.
    But this is precisely why I asked the specific question whether you were advocating 30 mA RCD protection for couplers as well!
    In fact, I agree it's a difficult situation to grasp, but at the end of the day the Reg exists for "couplers" separate to "socket-outlets", and I can't see the difference between "appliance outlet" and "free outlet" in the context of a cable coupler.
    So, the question - should couplers be included in 411.3.3 ? I sort of think you're saying they should be.
    Agreed. 411.3.3
    Yes, but not quite, 411.3.3 (ii) may apply in some cases?
    I think this is a socket-outlet, or an accessory with socket-outlets, so I think 411.3.3 (i) applies.
    Unless 411.3.3 (ii) applies, I believe so. This is definitely a cable coupler, and these do not appear to be covered by 411.3.3 (i)
    Disagree. If the panel outlet complies with BS 5733 and has a connector block for "hard wiring", then this would comply with BS 7671, and I don't think it needs an RCD unless 411.3.3 (ii) applies, as there are no socket-outlets, just couplers.
  • Bob C:
    Apologies for the apparent tangents - we're still debating the finer points.
    So far we seem to agree that if the PDUs contain BS 1363 socket outlets then the 30mA RCD requirements would apply - so somehow or other that would need to be dealt with - either by a 30mA RCD in the supply circuit, or one or more 30mA RCDs within the PDU arrangement (or better still by risk assessment to eliminate the need for RCDs altogether - probably what most PDU manufacturers assume). Ditto if there are BS EN 60309 sockets (or even BS 546 sockets) rated 32A or less within the rack.
    We seem to have mixed opinions still if other types of 'connectors' are used - e.g. the IEC 60320s chassis mount outlets often found on PDUs.
    To me, trying to supply an IT rack without an risk assessment to omit 30mA RCDs is rather like trying to run a taxi service without a driving licence - while it's not impossible, the contortions you have to go through (hard wiring things that should be pluggable, perhaps needing 30mA RCDs when they're not really needed) make it a very dubious choice in the long run.
  • AJJewsbury:
    Bob C:
    I agree with Andy for the most part. It's probably get the risk assessment, or fit the RCDs to be honest ... the appliance-outlet is a technicality (and only that). If a client's not happy with the risk assessment, they won't be happy getting out of the RCD on such a technicality anyway!
    But BS 7671's definition of a socket outlet specifies that it's 'installed with the fixed wiring' (which I take to mean connected to the fixed wiring rather than at the same time as the fixed wiring) - sockets one the end a bit of free flex doesn't seem to match that at all. They do seem to match BS 7671's definition of a Connector though.
    Life would be so much simpler if BS 7671 definitions just said that equipment was a 'xyz' if it complied with a standard that had the word 'xyz' in its title (not least in the old "is an FCU a distribution board?" debate) - but whether through historical accident or otherwise, JPEL/64 seem to have its own opinions on such matters. We surely can't just ignore Part 2 when reading BS 7671?
  • Guys, thanks for the responses it is much appreciated. Our Client appears to be going down the route of an Isolator to supply the Cabinet with an IEC Connector in the rack. I still have concerns on this arrangement because the connectors in my opinion are effectively still sockets (albeit non standard) that can be plugged/unplugged to suit the rack's internal configurations. I would be much happier with this set-up if the Client provided a Risk Assessment so I could insert a condition that any internal power re-configuration is carried out by a Qualified Electrician and not an IT Technician, not perfect but gives a bit of comfort.
    I have a situation where some of the IT cabinets are 3 Phase and I dread the thought of an IT Technician interconnecting the power to dual fed Servers for obvious reasons.
    Bob C
  • Bob C:
    I wouldn't worry about that, provided the outlets are single-phase. In servers or network with multiple PSUs, they are usually single-phase only, and the supplies are not "bussed" on the AC side.
    Such equipment is made to use in situations where some of the supplies are connected to UPS. Even if the two separate supplies were on the same phase (albeit potentially from different transformers in redundant supply situations), the UPS is not "phase locked" with the live supply (or another UPS), and therefore you might get times where there's 480 V between Line conductors (of the separate supplies), but each enclosed PSU only sees 230 V to earth (and hopefully Neutral).