"...address 1:
LV underground - 362m
HV underground to primary- 2000m
No Surge protection devices
For addr1, ignore the HV (e.g. use zero for Lpah Lpch), then take Lpcl as 362 and Lpal as 638 ?
LV underground to substation - 110 m
HV UG from substation to HV pole is 823m then 301m 11kV overhead then 190m HV UG to the primary substation.
Distance to cable termination with surge protection device from secondary substation is 1124m (823m 11kV UG + 301m 11kV Overhead). The nearest cable
termination does not have surge protection installed. ..."
"...address 1:
LV underground - 362m
HV underground to primary- 2000m
No Surge protection devices
For addr1, ignore the HV (e.g. use zero for Lpah Lpch), then take Lpcl as 362 and Lpal as 638 ?
LV underground to substation - 110 m
HV UG from substation to HV pole is 823m then 301m 11kV overhead then 190m HV UG to the primary substation.
Distance to cable termination with surge protection device from secondary substation is 1124m (823m 11kV UG + 301m 11kV Overhead). The nearest cable
termination does not have surge protection installed. ..."