my surge protection 'cpd', such as it is...

Good morning all


I have obtained the following [I feel as the] 'best we can do for now' information from the DNO. They were helpful in my test case request for info.


"...address 1:

LV underground - 362m

HV underground to primary-  2000m

No Surge protection devices


address 2:

LV underground to substation - 110 m

HV UG from substation to HV pole is 823m then 301m 11kV overhead then 190m HV UG to the primary substation.

Distance to cable termination with surge protection device from secondary substation is 1124m (823m 11kV UG + 301m 11kV Overhead).  The nearest cable

termination does not have surge protection installed. ..."


In relation to the risk assessment equation variables dealing with distribution cable lengths  ie. the Lpal Lpcl Lpah Lpch, how would one fit the given values into the variables ?


For addr1, ignore the HV (e.g. use zero for Lpah Lpch),  then take Lpcl as 362 and Lpal as 638 ?


For addr2, i'm not sure on this one ?


Thanks for your input.

Habs


Parents

  • gkenyon:




    psychicwarrior:


    Interesting re: the phone line concerns - perhaps all one can do, given it belongs to the phone company up to the master socket and is not BS7671, is advise the client that it too needs looking at and to contact the supplier to have it assessed - or can someone fit something themselves without messing with the master socket - will have to have a read. Then there is fibre (dependng on construction materials) to consider...Or is it really immune as one might think.


    Thank you all again.




    The requirement in BS 50174-3 (referred to from BS 6701 and BS 7671) is to fit SPDs "at all building entrances if the IT cable contains metallic cable elements, and where inadequate protective measures have been provided in the external IT network".


    ...



     

    Is this saying that if considering/provisioning SPD, 'we' have to do so for everything else too ; should we be inspecting Comms, IT/Data installation cabling and SPD equipment, as a result of the indirect link in 7671 in that case, after the point it becomes not-the-suppliers concern of course. If so, where would such findings get recorded. Maybe time for a new section in Special Installations.


Reply

  • gkenyon:




    psychicwarrior:


    Interesting re: the phone line concerns - perhaps all one can do, given it belongs to the phone company up to the master socket and is not BS7671, is advise the client that it too needs looking at and to contact the supplier to have it assessed - or can someone fit something themselves without messing with the master socket - will have to have a read. Then there is fibre (dependng on construction materials) to consider...Or is it really immune as one might think.


    Thank you all again.




    The requirement in BS 50174-3 (referred to from BS 6701 and BS 7671) is to fit SPDs "at all building entrances if the IT cable contains metallic cable elements, and where inadequate protective measures have been provided in the external IT network".


    ...



     

    Is this saying that if considering/provisioning SPD, 'we' have to do so for everything else too ; should we be inspecting Comms, IT/Data installation cabling and SPD equipment, as a result of the indirect link in 7671 in that case, after the point it becomes not-the-suppliers concern of course. If so, where would such findings get recorded. Maybe time for a new section in Special Installations.