psychicwarrior:
gkenyon:
psychicwarrior:
Forgive me to come back to this again, but...
Take a *row* of small shops in a town centre all joined together, just for instance. e.g. Urban, commercial and no LPS on the row.
Reading the Regs, it is mentioned that SPDs are for transients from atmospheric and from switching - but it details that concern is for switching from *within* the installation only, as I read it.
Therefore if the example shop is not concerned with internal switching i.e. it only has a till and some lights, then the concern is only with atmospheric.
Given a shop is a commercial activity, a risk assessment approach cannot be taken and Regs state fit a SPD; as an aside, this applies it seems, even if it is a shop selling junk and a shop floor the size of a six-pence and a domestic probably has more 'value' in it. Given there is no LPS on the shop (or the row of), then its a TYPE 2 SPD near the origin (well, in the shop DB). Correct please ?
oh and only when an LPS is fitted is a TYPE 1 required too (or a 1+2). ?
Regards
HabsAll of these questions are answered in sections 3.7.2 and 3.7.3 of the OSG (pp39-41 of the current edition).
My good man, with respect I say, as are a lot of questions raised on here covered/answered in the usual and other publications !
I am sorry my question caused that big sigh from you :-) I do read before I ask anything...perhaps that just makes it worse haha
A simple brief yes, no discussion perhaps just to see if I understood what I read.
Take a *row* of small shops in a town centre all joined together, just for instance. e.g. Urban, commercial and no LPS on the row.
Reading the Regs, it is mentioned that SPDs are for transients from atmospheric and from switching - but it details that concern is for switching from *within* the installation only, as I read it.
Therefore if the example shop is not concerned with internal switching i.e. it only has a till and some lights, then the concern is only with atmospheric.
Given a shop is a commercial activity, a risk assessment approach cannot be taken and Regs state fit a SPD; as an aside, this applies it seems, even if it is a shop selling junk and a shop floor the size of a six-pence and a domestic probably has more 'value' in it.
Given there is no LPS on the shop (or the row of), then its a TYPE 2 SPD near the origin (well, in the shop DB). Correct please ?
oh and only when an LPS is fitted is a TYPE 1 required too (or a 1+2). ?
psychicwarrior:
gkenyon:
psychicwarrior:
Forgive me to come back to this again, but...
Take a *row* of small shops in a town centre all joined together, just for instance. e.g. Urban, commercial and no LPS on the row.
Reading the Regs, it is mentioned that SPDs are for transients from atmospheric and from switching - but it details that concern is for switching from *within* the installation only, as I read it.
Therefore if the example shop is not concerned with internal switching i.e. it only has a till and some lights, then the concern is only with atmospheric.
Given a shop is a commercial activity, a risk assessment approach cannot be taken and Regs state fit a SPD; as an aside, this applies it seems, even if it is a shop selling junk and a shop floor the size of a six-pence and a domestic probably has more 'value' in it. Given there is no LPS on the shop (or the row of), then its a TYPE 2 SPD near the origin (well, in the shop DB). Correct please ?
oh and only when an LPS is fitted is a TYPE 1 required too (or a 1+2). ?
Regards
HabsAll of these questions are answered in sections 3.7.2 and 3.7.3 of the OSG (pp39-41 of the current edition).
My good man, with respect I say, as are a lot of questions raised on here covered/answered in the usual and other publications !
I am sorry my question caused that big sigh from you :-) I do read before I ask anything...perhaps that just makes it worse haha
A simple brief yes, no discussion perhaps just to see if I understood what I read.
Take a *row* of small shops in a town centre all joined together, just for instance. e.g. Urban, commercial and no LPS on the row.
Reading the Regs, it is mentioned that SPDs are for transients from atmospheric and from switching - but it details that concern is for switching from *within* the installation only, as I read it.
Therefore if the example shop is not concerned with internal switching i.e. it only has a till and some lights, then the concern is only with atmospheric.
Given a shop is a commercial activity, a risk assessment approach cannot be taken and Regs state fit a SPD; as an aside, this applies it seems, even if it is a shop selling junk and a shop floor the size of a six-pence and a domestic probably has more 'value' in it.
Given there is no LPS on the shop (or the row of), then its a TYPE 2 SPD near the origin (well, in the shop DB). Correct please ?
oh and only when an LPS is fitted is a TYPE 1 required too (or a 1+2). ?